So, I have a question that I can't really get a straight answer to. I recently installed two 8ft baseboard heaters on the rental side of my house. They are both on the same circuit, controlled through a wall thermostat to kick them both on and off at the same time.
So here is how the circuit is layed out. Double 20 amp breaker to provide 240 volts. All the wiring is 12/2. From the breaker, out into the thermostat. Then out of the thermostat, into a junction box. The wire then splits into 2 12/2 lines, one for each heater.
My issue is, each heater is 10.5 amps. There is a total load of 21 amps on the section of the circuit from the breaker, to the junction box where it splits. From what I've been told, 12 gauge wire is rated for 20 amps. Once the heaters run for a while, the section of wire before the junction box will get a little warm. Not hot, just a little warm. So I am wanting to replace the run of wire from the breaker to the junction box with 10 gauge, and leave the 12 gauge running to each heater, because 12 gauge is plenty thick to run the 10.5 amps that they will be carrying.
Is this ok to do? I've heard yes, and I've heard that if any part of the circuit is 10 gauge, it all has to be 10 gauge. I'm thinking it should be fine, because the wire will be correctly sized for the amperage it will be carrying at each area of the circuit, and it is a dedicated circuit for the heaters, nothing else will ever be added. I really would rather buy a 50ft roll of 10 gauge to replace the 21 amp load section, than buy a 250 ft roll for 200 dollars and rewire the whole circuit with it.
Thanks to anyone with any help
So here is how the circuit is layed out. Double 20 amp breaker to provide 240 volts. All the wiring is 12/2. From the breaker, out into the thermostat. Then out of the thermostat, into a junction box. The wire then splits into 2 12/2 lines, one for each heater.
My issue is, each heater is 10.5 amps. There is a total load of 21 amps on the section of the circuit from the breaker, to the junction box where it splits. From what I've been told, 12 gauge wire is rated for 20 amps. Once the heaters run for a while, the section of wire before the junction box will get a little warm. Not hot, just a little warm. So I am wanting to replace the run of wire from the breaker to the junction box with 10 gauge, and leave the 12 gauge running to each heater, because 12 gauge is plenty thick to run the 10.5 amps that they will be carrying.
Is this ok to do? I've heard yes, and I've heard that if any part of the circuit is 10 gauge, it all has to be 10 gauge. I'm thinking it should be fine, because the wire will be correctly sized for the amperage it will be carrying at each area of the circuit, and it is a dedicated circuit for the heaters, nothing else will ever be added. I really would rather buy a 50ft roll of 10 gauge to replace the 21 amp load section, than buy a 250 ft roll for 200 dollars and rewire the whole circuit with it.
Thanks to anyone with any help